    Default disarming ademco partition from access cntl.

    Hi there. This is my first post so I'll try not to embarrass myself.
    I need to disarm a partition on an "Ademco" Vista 128 alarm panel from my "Keyscan" ACU4300 access control panel. I'm using the keyswitch input (zone77) on the Ademco, and it needs a 2 second dry contact closure but all I have from my Keyscan is a latched dry contact. So does anybody know what I need to do? Do I have to make a circuit with a 555 timer and a relay or are there products out there to do this? Any advice would be appreciated.
    thanks

  2. #2
    Join Date
    Sep 2006
    Location
    Bentonville, AR
    Posts
    3,011

    Default

    This should do the trick. You can configure it for seconds or minutes, trigger the relay on the start or end of timing cycle, etc. Extremely versatile. Available at every security distributor. Probably under $20, don't remember, could be half that.
    http://www.altronix.com/index.php?pid=2&model_num=6062

    Other timer relays from Altronix.
    http://www.altronix.com/index.php?kw...id=2&Submit=Go
    Last edited by integrator97; 10-22-2009 at 11:23 PM. Reason: tipo :)

    Rocket Science
    Making everything else look simple, since 1958.


    http://my.opera.com/integrator/blog/
    One Man's Opinion

    The Future. It isn't what it used to be.

  3. #3
    Join Date
    Oct 2009
    Posts
    6

    Default Yay!

    Thanks a million. Exactly what I need.